Home Forums Archives Delfield 407CA Freezer won’t start. Replaced the cap, relay and thermo already and compressor has resistance between legs and open to ground. Does the fan have to start before compressor will start? What else could it be. It has 404 in it.

  • Delfield 407CA Freezer won’t start. Replaced the cap, relay and thermo already and compressor has resistance between legs and open to ground. Does the fan have to start before compressor will start? What else could it be. It has 404 in it.

    Posted by guest on April 22, 2019 at 12:00 am

    I wish they would at least put one service valve on these units.

    fixbear replied 4 years, 11 months ago 1 Member · 3 Replies
  • 3 Replies
  • eritech1

    Member
    April 22, 2019 at 8:57 am

    Are u getting power to ur compressor?

    Wat type of controler do u have? Do u have a defrost timer?

  • fixbear

    Member
    April 22, 2019 at 11:21 am

    Delfield’s electronic control is programmed to start in defrost.    Plug in the freezer and wait 40 min.  It has to initialize.  Door must be closed.  It will then test cycle the evaporator fan, condenser fan, and compressor.  Once the compressor and condenser fan starts and runs constant,  the evaporator fan will start after the coil cool’s to below freezing.

  • fixbear

    Member
    April 22, 2019 at 12:26 pm

    I forgot, this manual explains it.  Make sure you are reading for FREEZER.

    https://www.partstown.com/modelManual/DEL-4SERIES_spm.pdf