– Urgent – Blast Chiller Problems – Urgent –
Hello Hello!Â
Â
This one’s gonna be for all the refrigeration techs out there,
Â
I am running into an issue with my T40 blast chiller, Its giving me the error code “All 14” which means its not getting cold enough fast enough.
Â
This unit has 3 modes, 38* Blast, 38* Hard blast and 0*
Â
From what I observed it will pull the room down to whatever temp you set it for and keep it at that temp, maybe a little below.Â
Â
Problem is, there is a problem and its not doing it good enough. I went to the compressor and checked it out, found a leak on the high side service valve which bothered me so i fixed it and then put some refrigerant in until I cleared the sight glass,Â
Â
Here’s what I got
Â
Compressor is: 3DB3F33KE-TEC-200 made by Copeland
Condensing unit is: W075L6-IT3A-3166 made by Trenton
Â
LL: 258 PSI, Liquid pipe temp: 93.6* F
SCL 12.6*
Â
SL: 12 PSI, Suction pipe temp: 14.3*F
SH: 40.4*
Â
Then today I went to check it out again and its all different, compressor would shut off and the suction would go into a 8″ vacuum so I adjusted cut in and cut out per Trentons install and service manual and the compressor started short cycling, my suction pressure with the room above 30* would be around 15-16 PSI but as it pulled down, the pressure went down to running about 4 PSI until eventually, the box reached temp and I set the LPCO to kill compressor at about 1 PSI.
Â
I added about 1 lb yesterday, not a lot for a system like this I would think but seemed to clear the SG. I saw bubbles in it again today so I added a couple of ounces and it cleared again.
Â
Having hit the 10-12* SC I would think my solid column of liquid is there so I would need to dial in the SH using the TXV which I started doing and the box hit temp again so I am letting it warm back up and will see what effect it had.
Â
Also, after having the comp run for a little bit the suction line became around -20 F and started frosting on the compressor that was as the box was getting to 0* F and the suction PSI was around 4 or 5.
Â
Any advice would be awesome, I am pretty much on my own and trying to get help from Delfield, Trenton A.K.A Keep Rite and HVAC Talk, I haven’t serviced a blast chiller before nor has anyone I work with.