    Posted by guest on October 22, 2015 at 12:00 am

    My Beverage-AirMT45 cooler is blowing warm air and the compressor does    not appear to be kicking on. Any suggestions?

    fixbear replied 8 years, 5 months ago 1 Member · 2 Replies
  • 2 Replies
  • abialas

    Member
    October 23, 2015 at 1:18 pm

    Hey Karl,

     

    I got this response from Beverage Air:

    If your compressor is not kicking on, that is the problem. It could be as simple as the compressor starting components or it could be the compressor itself.

    They suggest you have a technician take a look at it to verify which part of the compressor is failing.

     

    Any more questions or issues please let us know

    – Anthonie Bialas

  • fixbear

    Member
    October 31, 2015 at 10:58 am

    You have many possible’s here. Is the compressor hot? is the condenser fan running? Is the temp control on? Is the condenser plugged in?

         Verify these to narrow it down. You can then test for power in the compressor starting terminals and overload. If there is a sign of restricted airflow for the condenser it will cause the overload to fail.

    Airflow problems and overload causes are condenser fan not running, plugged condenser, blocked vents, and overcharge.