    Posted by guest on April 21, 2018 at 12:00 am

    I HAVE A BALDOR 3PHASE MOTOR ON A CAROUSEL EXHAUST FAN IN WHICH THE SYSTEM STOPPED WORKING. THERE IS POWER FROM THE BREAKER BOX TO THE FUSE BOX TO THE ADJACENT BOX WHICH I HAVE NO KNOWLEDGE NO [POWER FROM THAT UNKNOWN BOX TO CONDUUIT6 TO MOTOR

    fixbear replied 5 years, 11 months ago 1 Member · 1 Reply
  • 1 Reply
  • fixbear

    Member
    April 21, 2018 at 8:33 pm

    If it is a 3 phase motor, it has to have a motor controller/contactor.  Usually with overloads. If you have voltage to all 3 poles of the top of the contactor phase to phase, then your input power is ok.   Next see if the contactor is closing. If not it will take a bit of tracing out why.  I don’t know what you have for control, buttons or switch or interlock with your hood system or a machine.

     

    I don’t have any idea of what you know or what meters and test equipment you have. If you aren’t comfortable with electricity, hire a electrician