  • Beverage Aire Coca Cola Cooler

    Posted by Anonymous on October 10, 2022 at 10:28 am

    Hi All,
    I have a Beverage Aire Coca Cola cooler I found at a deal. I replaced the complete skid and the thermostat. This things is working like a dream but for some reason the thermostat is not kicking the compressor off when the desired temperature is reached. I can control the compressor by turning the thermostat knob but its just not killing the power to the compressor the way it should automatically. I’m a DIY kinda guy but this has got me stumped. Any direction would be appreciated.

    fixbear replied 4 years, 1 month ago 2 Members · 1 Reply
  • 1 Reply
  • fixbear

    Member
    October 10, 2022 at 1:45 pm

    First, how long did you run the unit? The coil has to get into the teens before even on a warm setting it will open. Cooler is made to operate between 28F and 39F. Designed with a 15F to 20F takedown across the evaporator coil to hold product below 40F. Only beverage that freezes at 32F is water. Sugar and alcohol drinks will run colder.

    It’s either the thermostat is the wrong one or the sensing bulb is not properly bonded to the evaporator coil. It should be a Ranco A12 series, not a A30. A30’s will cause freeze ups at times. A-12’s have a fixed cut in temp of 36, 37, or 38 degrees ( depending on model) F to facilitate de-icing every cycle. Cut out will be between 9F and 18F. Thats’ why they have to sense the actual coil temp, not the cabinet air temp. A30’s vary both the cut out and cut in with setting and have a fixed range. A30’s will work with low usage as a air temp thermostat but will eventually have ice up problems with higher humidity’s or heavy usage. But they do have to sense on the discharge side of the evaporator.

Log in to reply.