Posted by beef on January 25, 2021 at 5:46 pmCustom RIC, 3 month old compressor and 3 txvs.
110psi suction over 400psi head. Compressor pumps down. Any ideas?
fixbear replied 5 years, 9 months ago 3 Members · 7 Replies -
7 Replies
-
R404a refrigerant
-
That head is way to high for R404. Even if it was a Kiln Tell me more about the system. Why 3 TXV’s, is it a rack system? What type of condenser? What temp are the cooled spaces at?
-
Should be 35 in box, but it’s at 55-60f.
Txv for each evap. Not a rack, sled in its own compartment. Custom self contain drawer cooler
-
Sounds like either a TXV is flooding and overcharge. Or you have non condensable’s in the system. That happens often with a incomplete vacuum and recharging with used R404.
What is the compressor and how many amps is it drawing?
-
Are you using a 4 valve manifold?
-
My firsth thought is non condensables.
-
Hey Beef, How did you make out with this?