Home Forums The Hot Side Hobart mixer HL200 Keeps tripping the gfci after running for a couple minutes.

  • Hobart mixer HL200 Keeps tripping the gfci after running for a couple minutes.

     fixbear updated 3 weeks ago 4 Members · 5 Posts
  • darioveliz

    Member
    July 17, 2020 at 5:42 am

    Hobart HL200 Legacy

  • ectofix

    Member
    July 17, 2020 at 2:21 pm

    Maybe the controls, the VFD or the motor has gotten wet during cleaning.

    Have you plugged it into a different GFCI to see if you get the same results?

  • fixbear

    Member
    July 17, 2020 at 4:07 pm

    Like Ectofix said, there is a bleed of electricity to the ground system somewhere. We are talking Milli-amps here. Finding the source can be a bit daunting. It can be some dust or flour that has some moisture to it. Oil track, The use of a Megger can help if you know how to use one. Other wise a quality ohm meter and individual isolation of elements will work.

    To eliminate a bad GFIC, go inside the machine power connection cable and open the ground wire to place a milliamp meter in series of the ground curcuit.. If you see over 5 milliamps, Then you need to find it inside the machine. Less than 5ma means your GFIC is bad.

    • ankorite

      Member
      July 17, 2020 at 7:15 pm

      Great points! I would like to add that a GFCI trips when the cumulative leakage for all the connected appliances goes over the threshold (5ma). If there are other things plugged into the same GFCI the HL200 might just be the “straw that broke the camels back”.

      My preferred method for finding leakage current is to use a clamp meter that can read milli-amps and then clamp around the hot wire and the neutral. Any measured milli-amps from this test would be leakage.

  • fixbear

    Member
    July 17, 2020 at 8:12 pm

    I forgot to mention one important point that often is overlooked. That’s where the GFI is at. If close to the load, not a problem. But if it’s a long distance away you can get induced current in the ground wire. I have seen over 300 volts on a support wire for overhead before the telephone company installed ground stakes at every pole. I’ve also seen farm fences with high induced voltages that run parallel to power lines. There are higher value GFI’s available for commercial use. Up to 8 ma.