prep bar problem
Posted by Anonymous on May 14, 2024 at 3:36 pmI have a Master-Bilt salad bar that is cooling way too much. It gets down to -15 and stays there. Its being controlled by a Johnson controls a419 controller. Double checked wiring and set points and its all good. The thermo stops at the right temp but the compressor just keeps going. Any ideas?
fixbear replied 2 years, 5 months ago 5 Members · 7 Replies -
7 Replies
-
You could have a dirty coil among many other possibilities. its hard to say with limited information. a model and serial could help. the sequence of operation is needed to properly diagnose.
-
model # for the bar is SPT-48
serial # is MW101358
-
Double checked the coils and their both good. Just to clarify, the coils aren’t freezing, its the air in side that’s freezing cold.
-
-
I’d check the thermistor and for a stuck relay on the controller.
-
not sure how to bench test the thermistor but I tried two different ones and got the same results. I’ll have to check those relays though….
-
-
Several different possibilities here. Is this the original controller or a replacement? If a replacement, what positions did you place the jumpers? What did you set as a dwell/differential? Hopefully it hasn’t had the wiring for the defrost heater miss-wired or cross wired with the compressor.
The PTC (thermistor) can be tested with a ohm meter. Johnson will have specs on it.
You can find the 419 page here:A419 Series Electronic Temperature Controls with Display and NEMA 1 or NEMA 4X Watertight Enclosures Technical Bulletin • Viewer • OpenBlue, Building Automation and Controls Knowledge Exchange (johnsoncontrols.com)
docs.johnsoncontrols.com
HTTP Status 400 – Bad Request
HTTP Status 400 – Bad Request
-
Several different possibilities here. Is this the original controller or a replacement? If a replacement, what positions did you place the jumpers? What did you set as a dwell/differential? Hopefully it hasn’t had the wiring for the defrost heater miss-wired or cross wired with the compressor.
The PTC (thermistor) can be tested with a ohm meter. Johnson will have specs on it.
You can find the 419 page here:A419 Series Electronic Temperature Controls with Display and NEMA 1 or NEMA 4X Watertight Enclosures Technical Bulletin • Viewer • OpenBlue, Building Automation and Controls Knowledge Exchange (johnsoncontrols.com)
By the way, there is no SPT-48 model in Masterbuilt.
docs.johnsoncontrols.com
HTTP Status 400 – Bad Request
HTTP Status 400 – Bad Request