  • True TSSU-48 Freezing up

    Posted by bruceb603 on December 27, 2020 at 11:41 am

    True Lowboy Freezing- We have a True TSSU-48 that is freezing up completely. We have the temperature contralto the lowest setting. Is it just the Temp Control kit that would need replacing or is it something else? The coils are cleaned and dust free.

    Sparky0575 replied 3 years, 2 months ago 4 Members · 4 Replies
  • 4 Replies
  • fixbear

    Member
    December 27, 2020 at 1:58 pm

    First defrost it and set the temp control to the middle of the range. Assuming you have a mechanical temp control. Watch for build up and raise it if it does. Make sure to check the door gaskets and for any source of water retention like a faulty drain line or leaking evaporator pan. They will increase icing drastically. Also uncovered warm product.

    Often the controls get replaced with the wrong one or not bonded to the evaporator coil. With The common replacements that are usually made by Ranco, the A-32 series moves both the cut in and cut out temperature. But the proper A-12 ones have a fixed cut in of between 36 and 39 degrees (depending on model) to facilitate defrost every cycle.

  • fixbear

    Member
    December 27, 2020 at 2:11 pm

    I forgot to mention that with the TSSU’s You can not have any product touching the back wall or within 4 inches of the evaporator. Doing so obstructs the air flow.

    And that they also do not, repeat do not measure the box temp. The control measures the evaporator coil temp. That’s why air flow is so important.

    BTW, what is the full model number? It’s not a prep table is it? They have unique problems of there own.

    • bobtech

      Member
      December 27, 2020 at 3:52 pm

      Is this a cap tube or TXV system?

      if a cap tube system the thermostat sensor is usually located near the middle of the evaporator. if low on charge, or the cap tube is partially restricted, the thermostat will not sense the proper temperature and the coil will ice up.

  • Sparky0575

    Member
    February 17, 2021 at 12:04 pm

    I have seen where evaporator plates started to separate that can cause this issue as well. thats is after you confirm that machine is leak free and charged correctly.