When performing preventative maintenance on an HVAC unit, it’s important to note any changes, especially repetitive issues, in airflow, temperatures, pressures, cycling and more. During a preventive maintenance inspection, technicians should look for changes in:
- Supply and return air temperatures
- Static pressure
- Airflow
- Motor and compressor amperage
- Voltage and phase balance
- Capacitor readings
- Contactor condition
- Refrigerant pressures
- Superheat and subcooling
- Discharge temperatures
- Motor and bearing temperatures
- Noise and vibration
- Cycle frequency and runtime
- Condensate production
- Control history and fault codes
Start With the Equipment History
Before getting the unit open, review the past operating and service history. This may reveal intermittent problems that may not be active while you’re taking a look at it. Look for:
- Repeated comfort complaints
- Recent breaker trips
- High-pressure or low-pressure alarms
- Freeze-stat trips
- Flame-failure or ignition faults
- Increasing runtime
- Repeated condensate alarms
- Frequent filter replacement
- Previous refrigerant additions
- Recurring motor or belt adjustments
- Multiple resets without a documented repair
Follow Required Safety Procedures Before Inspection
Before performing work that requires energy isolation:
- Identify every energy source.
- Notify affected personnel as required.
- Shut down the equipment normally.
- Isolate applicable energy sources.
- Apply lockout/tagout devices under the employer’s procedure.
- Control stored or residual energy.
- Verify that isolation is effective.
- Follow approved restoration procedures after service.
Look for Reduced or Unbalanced Airflow
Reduced airflow is one of the most common indicators of an HVAC issue. It can be caused by a variety of components. Check:
- Filter condition and pressure drop
- Evaporator and heating-coil cleanliness
- Blower-wheel condition
- Fan rotation
- Belt tension and alignment
- Pulley and sheave condition
- Motor speed and amperage
- Damper position
- Supply and return restrictions
- Diffuser or register airflow
- External static pressure
- Pressure across major components
Compare Supply and Return Air Temperatures
Measure temperatures using suitable instruments and consistent test locations. Consider:
- Indoor dry-bulb temperature
- Indoor wet-bulb temperature or relative humidity
- Outdoor ambient temperature
- Equipment load
- Fan speed
- Filter and coil condition
- Economizer position
- Reheat or supplemental heat operation
- Manufacturer specifications
Inspect Electrical Connections for Heat and Deterioration
Inspect electrical compartments for:
- Darkened or melted insulation
- Loose or corroded terminals
- Pitted or welded contactor contacts
- Burned relays
- Swollen or leaking capacitors
- Damaged fuse holders
- Improper wire sizing
- Weak or broken terminal connections
- Water intrusion
- Insect or rodent damage
- Unapproved repairs
- Signs of overheating around lugs and breakers
Identify Voltage and Phase Problems
Check the manufacturer specifications to ensure the motors and compressors are getting the correct support from the electrical supply. Check for:
- Low or high supply voltage
- Voltage imbalance
- Current imbalance
- Missing phase
- Loose incoming conductors
- Damaged disconnects
- Failing fuses
- Contactor voltage drop
- Transformer problems
- Control-voltage instability
Test Capacitors Against Their Ratings
Signs of a bad compressor can show before issues with a motor or compressor arise. Early symptoms may include:
- Extended starting time
- Intermittent humming
- Higher starting current
- Motor overheating
- Contactor chatter
- Failure during high-load conditions
- Operation that improves after the unit cools
Examine Contactors, Relays, and Control Components
Signs of deterioration include:
- Excessive pitting
- Burned or discolored contacts
- Chattering
- Delayed pull-in
- Failure to release
- Coil overheating
- Unusual buzzing
- Loose terminals
- Excessive voltage drop
- Damaged housings
Listen for New Noise and Vibration
Potential warning sounds include:
- Grinding
- Scraping
- Rattling
- Knocking
- Squealing
- Humming
- Buzzing
- Bearing rumble
- Refrigerant pulsation
- Contactor chatter
- Fan-wheel contact
Inspect:
- Motor bearings
- Fan bearings
- Blower wheels
- Propeller fans
- Belts and pulleys
- Mounting bolts
- Equipment panels
- Compressor mounts
- Refrigerant piping supports
- Vibration isolators
- Duct connections
Check Belts, Sheaves, Bearings, and Blower Wheels
Belt-drive components can deteriorate over time and reduce airflow before a complete failure happens. Look for:
- Cracking or glazing
- Frayed belt edges
- Belt dust
- Excessive slack
- Uneven belt position
- Misaligned sheaves
- Worn pulley grooves
- Loose set screws
- Bearing play
- Lubricant leakage
- Excessive bearing temperature
- Dirt buildup on blower blades
Inspect Coils for Fouling, Damage, and Corrosion
Inspect evaporator and condenser coils for:
- Dust and grease buildup
- Matted debris
- Blocked coil depth
- Bent fins
- Corrosion
- Chemical residue
- Damaged coatings
- Oil staining
- Frost or ice
- Air bypass around the coil
- Poor condenser discharge clearance
Evaluate Refrigerant Conditions as a Complete System
Potential early warning signs include:
- Abnormal superheat
- Abnormal subcooling
- Low suction pressure
- High discharge pressure
- Unusual discharge temperature
- Flashing in a liquid-line sight glass, when applicable
- Frost in an unexpected location
- Oil residue at joints or components
- Repeated low-pressure or high-pressure trips
- Reduced capacity
- Long runtime
- Compressor overheating
Possible causes may include:
- Refrigerant leakage
- Restricted airflow
- Dirty coils
- Metering-device problems
- Liquid-line restriction
- Overcharge
- Noncondensables
- Moisture contamination
- Fan-performance problems
- Compressor inefficiency
- Incorrect control operation
Look for Oil Residue and Refrigerant-Leak Indicators
Inspect common leak areas such as:
- Service ports and caps
- Schrader cores
- Flare or mechanical joints
- Brazed joints
- Coil return bends
- Distributor tubes
- Filter-driers
- Pressure controls
- Accumulators and receivers
- Compressor terminals
- Vibration points
- Areas with tubing contact or abrasion
Check Compressor Starting and Operating Conditions
Watch for:
- Hard starting
- Delayed startup
- Increasing current
- Overload trips
- Short cycling
- Excessive shell temperature
- New vibration
- Knocking or rattling
- Abnormal suction or discharge conditions
- Declining capacity
- Extended runtime
- Oil staining around terminals or fittings
Identify Short Cycling and Excessive Runtime
Possible causes include:
- Incorrect thermostat or sensor location
- Control instability
- Refrigerant pressure-control trips
- Low airflow
- Dirty coils
- Oversized equipment
- Poor staging
- Safety-limit operation
- Drain or float-switch problems
- Building automation commands
- Improper setpoints
- Compressor overload operation
Inspect Condensate Drains Before They Cause a Shutdown
Condensate problems can create water damage, microbial growth, corrosion, nuisance alarms, and equipment shutdowns. Inspect:
- Drain-pan condition
- Rust or cracks
- Standing water
- Drain slope
- Trap design and condition
- Blocked drain lines
- Float-switch operation
- Condensate-pump operation
- Insulation around drain piping
- Water staining below the unit
- Biological buildup
- Negative-pressure drainage issues
Evaluate Burners, Ignition, and Combustion Components
Potential early warning signs include:
- Delayed ignition
- Repeated ignition attempts
- Flame rollout
- Unstable flame
- Burner corrosion
- Soot
- Unusual odor
- Flame-sensor contamination
- Igniter deterioration
- Heat discoloration
- Vent damage
- Frequent limit trips
- Inducer noise
- Condensate problems in condensing equipment
Inspect Economizers and Outdoor-Air Controls
Economizer problems can imitate refrigeration failures, create comfort complaints and increase energy use. Be sure to check:
- Outdoor-air damper position
- Return-air damper position
- Linkages and actuators
- Mixed-air sensors
- Outdoor temperature and humidity sensors
- Minimum ventilation settings
- Damper seals
- Control sequences
- Building automation commands
- Mechanical binding
Pay Attention to Moisture, Corrosion, and Contamination
Water intrusion and contamination often damage HVAC equipment over time. Look for:
- Rust trails
- Corroded terminals
- Water inside electrical compartments
- Failed cabinet seals
- Damaged conduit entries
- Standing water
- Biological growth
- Grease accumulation
- Salt or chemical corrosion
- Rodent or insect activity
- Deteriorated insulation
Use Trend Data to Find Problems Earlier
Useful PM data includes:
- Line voltage by phase
- Motor and compressor amperage
- Capacitor readings
- Supply and return temperatures
- Temperature rise
- Static pressure
- Filter pressure drop
- Superheat and subcooling
- Suction and discharge pressure
- Discharge-line temperature
- Bearing temperature
- Runtime and cycle counts
- Controller alarms
- Combustion readings
- Damper commands and positions
What Findings Require Immediate Escalation?
Examples may include:
- Burned or melting conductors
- Loose high-current connections
- Repeated breaker or overload trips
- Suspected gas leakage
- Flame rollout
- Damaged heat exchanger
- Unsafe combustion or venting
- Refrigerant release
- Severely overheating motors or compressors
- Failed safety controls
- Exposed moving components
- Major structural damage
- Significant oil leakage
- Water contacting energized components
- A fault that cannot be safely diagnosed
- Required guards or panels that cannot be reinstalled
HVAC Preventive Maintenance Failure-Detection Checklist
Before operating the equipment
- Confirm the model, serial number, and equipment configuration.
- Review previous work orders and recorded readings.
- Check for active alarms and operator complaints.
- Inspect the surrounding area for water, oil, damage, and access hazards.
- Review manufacturer service information.
- Identify electrical, mechanical, pressure, thermal, gas, and refrigerant hazards.
During the inspection
- Check filters and airflow restrictions.
- Measure static pressure where appropriate.
- Inspect coils and blower components.
- Measure supply and return temperatures.
- Inspect electrical connections and components.
- Record voltage and current by phase.
- Test capacitors using the approved procedure.
- Inspect contactors, relays, and control wiring.
- Listen for abnormal noise and vibration.
- Inspect belts, bearings, pulleys, and mounts.
- Evaluate refrigerant conditions using the OEM method.
- Look for oil residue and potential leak indicators.
- Check condensate drainage and safety switches.
- Inspect economizers and dampers.
- Evaluate combustion and venting on heating equipment.
- Review alarm, cycle, and runtime history.
Before leaving the site
- Correct or document every significant deficiency.
- Remove temporary diagnostic connections.
- Reinstall panels, guards, and covers.
- Verify normal operating sequence.
- Confirm that safety controls remain functional.
- Remove tools and loose hardware.
- Clean the work area.
- Record final readings.
- Explain urgent findings to the appropriate site contact.
- Clearly identify equipment that must remain out of service.