The Whalen Company Heat Pump Solid State Safety Control Board Terminal Identification

Component identification is vital for a tech learning to work on new HVAC equipment. This guide for The Whalen Company heat pump solid state safety control board terminal identification can help you get a more advanced understanding of the board and how it plays a role into the order of operations. 

This board is commonly found on The Whalen Company water-source heat pumps. 

The Whalen Company Heat Pump SS Safety Control Board Terminals

Terminal LabelNumber of TerminalsTerminal Info
RTN2Freeze protection sensor
WATER2Water temperature sensors
COND2Condensate sensor
C224 volt common terminal and they are common to each other
ALR1Alarm contact which is a dry contact
R224 volt power and are common to each other
CC1Compressor contact which sends power down to the chassis from compressor contactor
HPS2High pressure return and high pressure 24 volt power out
Y1Receives call from thermostat
WV1Water valve that upon a call from the thermostat, sends power to actuator valve in chassis if it’s equipped
LPS1Low pressure return

The Whalen Company Heat Pump SS Safety Control Board Jumpers

At the edge of the board, there are jumpers. These determine the temperature range of the water temp safety and the freeze temp safety

  • RTN TEMP jumper – This is the freeze sensor for the thermistor located on the suction line before the compressor. It’s set at 32 degrees when set from the factory.
  • WATER TEMP jumper – The water temperature jumper is set at 36 degrees when set at the factory. 
  • Alarm jumper – When the alarm jumper is in the pulse position it will send an audible clicking sound.
  • Test mode jumper – When this jumper is off, the unit operates as normal. If it’s put in on, it will operate with canceling anti-short cycling protection for a period of 1 hour upon start up. 

The Whalen Company Heat Pump SS Safety Control Board LEDs & Fault Codes

There are two LED lights on the control board. 

  • LED 2 – This is for the power and when the unit is operating properly, it lights up green.

What Do The Whalen Company Heat Pump LED Fault Codes Mean