Lochinvar Water Heater Troubleshooting

Water heater malfunctions come in a wide variety of problems, from displays not working to the burner malfunctioning. If you need help learning Lochinvar water heater troubleshooting, follow along with our guide below. We’ll help you get the water heater operational and ready for heating in no time. 

How Do I Troubleshoot a Lochinvar Water Heater?

ProblemCauseSolution
No displayNo voltage supplied to unit
Display board faulty
Main control board malfunctioning
Fuse is blown
Check external line switch, fuse and breaker
Check wire harness connection between display board and main control board
Replace faulty display board
Replace main control board
Replace fuse F3 on main control board
Burner not operatingTank temperature set point satisfied
Unit locked out on fault
Check temperature setting
Check display for specific fault
Unit doesn’t modulate over 50%Open flue sensorVerify flue sensor is located in flue outlet
Check wiring connections at flue sensor
Confirm flue sensor resistance is accurate
Noisy operationGas supply issue
Gas/air mixture problem
Dirty or damaged burner
Low water flow through the heat exchanger
Air in piping system
Check gas pressure is at correct levels
Verify that vent/air intake lengths don’t exceed maximum
Clean or replace burner as needed
Verify pump operation
Purge air from piping system
No pump operationFuse blown
Faulty pump
Faulty pump relay
Internal malfunction on control board
Replace fuse F5 on control board
Replace pump
Replace pump relay
Replace main control board
Relief valve openingSystem pressure exceeds relief valve settingLower system pressure below 150 PSI rating of supplied relief valve