  • 134a cap tube 0psi 105 high

    Posted by Anonymous on September 26, 2023 at 2:53 pm

    I have a reach in 134a captube that had 0psi low side and 105 high no cooling. Cap is clear drier is clear factory charge 13.4 oz. This is a cooler 35°.
    Everything is working evap and condensor fans. Coils are clean.
    I cannot figure this one out can anyone help?

    fixbear replied 7 months, 1 week ago 2 Members · 1 Reply
  • 1 Reply
  • fixbear

    Member
    September 26, 2023 at 7:28 pm

    It either has moisture in the system, you have a leak, or the cap tube is blocked. It May be that it is undercharged. Slowly add on the low side till the high side get’s the equivalent of 20 to 30 degrees above the high side ambient.

    If it starts cooling, Vacuum it out and discard the refrigerant and recharge. Make sure to use a micron gauge to less than 400.